Kontrollü başlatıcı 160 кW . motor 22 kW. Soft starter.

  • Konbuyu başlatan Konbuyu başlatan Johik
  • Başlangıç tarihi Başlangıç tarihi

Johik

Üye
Katılım
7 Haz 2018
Mesajlar
95
Puanları
1
Yaş
59
Good evening . Need advice on Schneider products.

Engine 22 kW. Soft starter -62A. Automatic switch for protection 63A.. The soft starter is out of order.

There is a soft starter ATS -22 160 kW in stock. If we change . Let's combine soft starter 160 kW with the engine 22 kW. What settings need to be made. Won't work AB 63A for protection?
 
63 A works for protection. You set the 160KW ATS settings to their minimum values.
 